For the first time in 18 years I had to use both buttons, when we had the big ice storm....Also when you use both buttons at the same time it ups the heat even more. They are so efficient though I've never had to do that.
For the first time in 18 years I had to use both buttons, when we had the big ice storm....Also when you use both buttons at the same time it ups the heat even more. They are so efficient though I've never had to do that.
Wow. I saw some of your pictures.of the snow. They were really beautiful however probably not fun to deal with. Ohio used to have some dozeys too. This year I had to use the higher button only a few times overnight. We've only had one real freeze that lasted over a week. And only one real snow. I don't recognize my home state.For the first time in 18 years I had to use both buttons, when we had the big ice storm....
You can brumate where you are without a fridge. I did it here three years in a row. I used one of my well insulated boxes and that averages out the day time high and night time lows. It wasn't cold enough for a Russian, but worked great for a Chersina, and would be great for a greek, hermanni, or a DT. There were a few warm winter spells where I had to let cold air in at night and run ice bottles during the heat of the day, but over all the box maintained things nice and cold in the shade.HOLY %^$# ... I can say with 100% confidence that that outlet was NOT a 20 amp line. That is clearly a 15 amp line and outlet. To avoid this completely and never have to worry about the outlet or wire in the wall I ran all brand new wire and outlets all rated for 20 amp.
I use the same 2 switch heaters 600, 900 and 1500 watt. I have an Inkbird 1800 watt temperature controller on it.. So I was thinking of taking the "tip over" device out completely as you said. What stopped me is their admission that materials and parts only are expected to be failure free for 1 year. Where in the hell is a 10 year warranty, even a 5 year? It's an oil filled heater not a device with moving parts and complex designs. The issue I have with heat is this ... The home is a 1965 mobile home and even in a room 9'x7' (master) 900 watts or more is needed to warm it up. I can just imagine how efficient 1965 insulation is, or was. It is clear I am wasting lots of money heating this structure BUT I have no other option. This year my wife and I are going to try and build a Tortoise House 20'x20' if financially we can swing it. This year None of our torts Brumated, not by our choice so we're stuck with this until it warms up. Plan better and next winter be in a position to Fridge brumate is the plan.
Thank you for the responses.
View attachment 366313View attachment 366314
This is what happened one day when I turned the heater on high for a quick bedroom warm up, walked away to tend to other stuff. Good thing I came back when I did. This was one of the original Delonghi oil filled radiator type heaters.
HOLY %^$# ... I can say with 100% confidence that that outlet was NOT a 20 amp line. That is clearly a 15 amp line and outlet. To avoid this completely and never have to worry about the outlet or wire in the wall I ran all brand new wire and outlets all rated for 20 amp.
This is not true, a 15 amp outlet will not handle 20 amps, it will start to burn. The wire size is what will dictate how much power can be used. So if you have a 15 amp wire but install a 20 outlet the "Fire" will start on the wire, somewhere in the wall usually because the wire is the weak point. If you install a 15 amp outlet on a 20 amp line it's the opposite, the outlet is the "Weak" point, so your fire will be at the outlet. The Breaker has to be sized to the wire size AS does the outlet. if your outlet is not properly sized to the wire and breaker you are just asking for a fire, either in the walls or at the wrong sized outlet. I happen to know a little about @Yvonne G house and know that her circuits for Lights and Outlets are 15 amp most likely (it's an older home). It is VERY common on older homes to have 15 amp circuits instead of 20 amp ones. ALSO if you have anything else plugged into that circuit you have to include THAT power draw as well. So even if the outlet, wire and breaker are sized right you can overload it by simply having a fan plugged into that circuit with the heater. You'll notice @Yvonne G did not say the breaker tripped. This circuit NEEDS to be inspected and make sure ALL is right Breaker size, Wire Size and Outlet rating. Most people assume that the Breaker will trip if ANYTHING happens, this is not true all the time.I think when you first posted this, I thought it was the plug being loose or not making good contact when plugged in. that or the plug was faulty or damaged. coulda been the outlet itself but that usually stays in the box.
the cord on the heaters are 16 gauge, they're rated for 1500 watts. even if it was a little more because of differences in voltage between outlet and heater, it wouldn't be enough to cause a problem. theres a decent amount of safety built in to the ratings/wire sizing.
Most 15 amp outlets are actually rated for 20 amps; as long as the breaker and wire match each other, it wouldn't cause a problem.
Thank you for this info. I would rather just use the fridge for peace of mind. This year has had so many issues with brumation for us. Gophers burying torts in burrows, 75 degree day followed by a 20 degree night then 45 degrees the next day and windy. I'm sure you can respect this ... with so many torts now to manage the fridge(s) would less finicky. I get the insulated box, but want an option that has less variables.You can brumate where you are without a fridge. I did it here three years in a row. I used one of my well insulated boxes and that averages out the day time high and night time lows. It wasn't cold enough for a Russian, but worked great for a Chersina, and would be great for a greek, hermanni, or a DT. There were a few warm winter spells where I had to let cold air in at night and run ice bottles during the heat of the day, but over all the box maintained things nice and cold in the shade
I asked the fireman that came why the breaker didn't trip. He didn't give me a satisfactory answer - I thought he really didn't know.This is not true, a 15 amp outlet will not handle 20 amps, it will start to burn. The wire size is what will dictate how much power can be used. So if you have a 15 amp wire but install a 20 outlet the "Fire" will start on the wire, somewhere in the wall usually because the wire is the weak point. If you install a 15 amp outlet on a 20 amp line it's the opposite, the outlet is the "Weak" point, so your fire will be at the outlet. The Breaker has to be sized to the wire size AS does the outlet. if your outlet is not properly sized to the wire and breaker you are just asking for a fire, either in the walls or at the wrong sized outlet. I happen to know a little about @Yvonne G house and know that her circuits for Lights and Outlets are 15 amp most likely (it's an older home). It is VERY common on older homes to have 15 amp circuits instead of 20 amp ones. ALSO if you have anything else plugged into that circuit you have to include THAT power draw as well. So even if the outlet, wire and breaker are sized right you can overload it by simply having a fan plugged into that circuit with the heater. You'll notice @Yvonne G did not say the breaker tripped. This circuit NEEDS to be inspected and make sure ALL is right Breaker size, Wire Size and Outlet rating. Most people assume that the Breaker will trip if ANYTHING happens, this is not true all the time.
This is not true, a 15 amp outlet will not handle 20 amps, it will start to burn. The wire size is what will dictate how much power can be used. So if you have a 15 amp wire but install a 20 outlet the "Fire" will start on the wire, somewhere in the wall usually because the wire is the weak point. If you install a 15 amp outlet on a 20 amp line it's the opposite, the outlet is the "Weak" point, so your fire will be at the outlet. The Breaker has to be sized to the wire size AS does the outlet. if your outlet is not properly sized to the wire and breaker you are just asking for a fire, either in the walls or at the wrong sized outlet. I happen to know a little about @Yvonne G house and know that her circuits for Lights and Outlets are 15 amp most likely (it's an older home). It is VERY common on older homes to have 15 amp circuits instead of 20 amp ones. ALSO if you have anything else plugged into that circuit you have to include THAT power draw as well. So even if the outlet, wire and breaker are sized right you can overload it by simply having a fan plugged into that circuit with the heater. You'll notice @Yvonne G did not say the breaker tripped. This circuit NEEDS to be inspected and make sure ALL is right Breaker size, Wire Size and Outlet rating. Most people assume that the Breaker will trip if ANYTHING happens, this is not true all the time.
I asked the fireman that came why the breaker didn't trip. He didn't give me a satisfactory answer - I thought he really didn't know.
I hear ya and agree. Just throwing out an alternative in case it was appealing for any reason.Thank you for this info. I would rather just use the fridge for peace of mind. This year has had so many issues with brumation for us. Gophers burying torts in burrows, 75 degree day followed by a 20 degree night then 45 degrees the next day and windy. I'm sure you can respect this ... with so many torts now to manage the fridge(s) would less finicky. I get the insulated box, but want an option that has less variables.
I appreciate it when you drop this knowledge. I learn from it every time.i think you said that your panel was upgraded when you got the solar, so it's a newer/ish panel so its unlikely you have the older breakers that failed often. But if you don't have arc fault breakers, then its likely that what happened wasn't something that would cause a normal breaker to trip (overcurrent).
arcing is what causes most electrical fires. outlet is 'loose', doesn't hold plug as firmly, theres arcing. its possible that the wiring at the outlet itself loosened over time, but like I said, that usually self extinguishes in the box.
So the panel upgrade DOES NOT upgrade the wires in the walls. Sorry about the spuratic responses trying to participate in this conversation and do tort chores (it's sunny today). I do not understand the whole 15 amp outlets on a 20 amp circuit. Every person on here I bet has seen an outlet thats burned, brown BUT the devices pluged into it still work as does the outlet. WHY they allow a 1500 watt heater (industry maximum) to be plugged into a 15 amp circuit and get hot being run 24/7 coming on and off and burn said outlet. I completely understand that it is not drawing enough to trip the breaker BUT running 12.5 amps with the initial inrush of power when cycling on and off will get that outlet AND cord hot. We've all had it happen I bet. So if you can explain why an outlet that IS going to get hot is allowed on a circuit ...I'm all ears. But if you just are searching this ? on google and do not understand the actual WHY ...I've already done that. The theory of electricity is a very complex thing.I appreciate it when you drop this knowledge. I learn from it every time.
Even this ... with all matched this 15 amp line, outlet and cord will get hot running a 1500 watt heater.Installing 15 amp receptacles on 20 amp circuits is common and perfectly within code. T.210.21(B)(3)
if her breakers are 15 amp, everything you said about it being a 15 amp receptacle is moot. ie they 'match' as you just said is required.
For those of us non technical people, how do we know what kind of outlets we have? Like I ASSUME my house has what is appropriate because there have been renovations in recent years, but what should I look for?So the panel upgrade DOES NOT upgrade the wires in the walls. Sorry about the spuratic responses trying to participate in this conversation and do tort chores (it's sunny today). I do not understand the whole 15 amp outlets on a 20 amp circuit. Every person on here I bet has seen an outlet thats burned, brown BUT the devices pluged into it still work as does the outlet. WHY they allow a 1500 watt heater (industry maximum) to be plugged into a 15 amp circuit and get hot being run 24/7 coming on and off and burn said outlet. I completely understand that it is not drawing enough to trip the breaker BUT running 12.5 amps with the initial inrush of power when cycling on and off will get that outlet AND cord hot. We've all had it happen I bet. So if you can explain why an outlet that IS going to get hot is allowed on a circuit ...I'm all ears. But if you just are searching this ? on google and do not understand the actual WHY ...I've already done that. The theory of electricity is a very complex thing.
I've been to the big box stores and seen all the bins full of electrical stuff. I wonder how many DIYers actually read about the outlet they're buying, or just grab one out of the bin.For those of us non technical people, how do we know what kind of outlets we have? Like I ASSUME my house has what is appropriate because there have been renovations in recent years, but what should I look for?
This is why I posed the question ....of why a 15 amp outlet that IS going to get hot is allowed on a 20 amp line. going to grab some outletsFor those of us non technical people, how do we know what kind of outlets we have? Like I ASSUME my house has what is appropriate because there have been renovations in recent years, but what should I look for?
So a outlet will say ALMOST always ONLY on the packaging the amperage. But when buying you look for 20 amp outlets. They are more and usually only 1 color, they will look identical as far as Prongs. There is a 20 amp only outlet that is used when there is ONLY 1 plug/outlet on the line and it has a horizontal prong, vertical and then ground.For those of us non technical people, how do we know what kind of outlets we have? Like I ASSUME my house has what is appropriate because there have been renovations in recent years, but what should I look for?
For those of us non technical people, how do we know what kind of outlets we have? Like I ASSUME my house has what is appropriate because there have been renovations in recent years, but what should I look for?